If you are looking to feed into the grid, please see our page on Victron DVCC
We are compatible with all Victron GX devices.
Products with an asterisk (*) only have a single CAN interface. If you are using other Victron devices (e.g. solar chargers) over VE.Can, you must make sure you pick our 250kbps Victron profile Reserved 14.

The procedure is similar for all GX devices, but the exact location of the port will vary. We suggest:

Custom Cable Pinout for Victron GX devices
| Function | VE.Can RJ-45 | Watchmon |
|---|---|---|
| GND | Pin 3 | Supply negative / ground |
| CAN-L | Pin 8 | CAN low |
| CAN-H | Pin 7 | CAN high |
For reference, here’s an Ethernet plug diagram. Be aware that some Ethernet Cables may vary as there are two (2) common wiring colour standards. Make sure that you inspect the plug on the Victron side and follow the wiring colour to the BMS terminal.

To make up the custom Ethernet Cable for the CCGX properly, you should use a proper crimper and fresh RJ45 male connectors. Label both ends of the cable and install it.
VE.Can to CAN-bus BMS Cables Manual

Outline above is for the TIA/EIA T568A straight-though connector outlined in blue below.


Open the WatchMon Toolkit and navigate to the Integration Settings by clicking the Menu then Hardware and select Integration Tab.
Select CANbus protocol to "Victron GX" (previously labelled Victron ColorControl GX) and Save.

On WatchMon Toolkit, navigate to the Control Logic menu, then the Charging tab.

Adjust the Charging Control Logic to suit the application.


Notes:
Navigate to Hardware, then the CellMon tab.

Adjust the CellMon Bypass Voltage to suit the application.

Note: Make sure to "Device Sync" the changes to the CellMons.
Navigate to the Remote tab on the Control Logic screen.


Notes:

Notes:
Navigate to Telemetry, then Live Stats to observe system operation.

Open the Victron software - VEConfigure settings
| Parameter | Setting |
|---|---|
| Battery type | Lithium |
| Charge curve vFixed | |
| Absorption voltage | 60.75 V |
| Float voltage | 60.00 V |
| Absorption time | 1 Hr |
Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 60.00 V.
This needs to be adjusted to match the BMS operating targets.
Select the fourth battery type:

Select the CAN-bus BMS (500 kbits/s) CAN profile in the Venus device. Menu path: Settings → Services → CAN-profile.
Note: This changes the function of a VE.Can port: it is not possible to connect both VE.Can products and a BMS battery together on a Color Control GX.

Select CAN-bus BMS (500 kbit/s)

After properly wiring and setting up, the BMS the ESS will be visible as a battery in the device list:

The Parameters option within the battery page shows the actual battery charge and discharge limits:

Yes.
Yes, when using the Victron CANbus profile (from software release 2.16 onwards).
Yes. Adopt the correct Control Remote configuration (from software release 2.17 onwards).
Not all the Victron products transmit back the optional actual values. Hence we cannot display these values if they are not transmitted from the GX.
The communication is not at fault, verify that the GX is sending the heartbeat RX timestamp to confirm communication is functioning properly.
No, the Victron CANbus protocol does not send these details. It expects the BMS to send these values.
Yes, if desired. Several customers have chosen to install both shunts in series, which is not ideal.
Yes, however, will limit the functionality since the BMS does not know the SoC% and cannot adjust its recommended charge and discharge targets.
Not recommended, only possible if 50mV for 500A, 1000A or 2000A.
Note: Please ensure that the firmware for all Victron Energy equipment is up to date. Details on how to check firmware versions and perform updates are available from the manufacturer directly.
Please know that this is deliberate. The BMS will limit the value it transmits to the inverter to 99% and not 100 until the charge is complete. This is because we want the inverter to continue to charge to allow the batteries to balance up to the threshold.
When complete, it transmits 100%. The system will also limit to 100% even if it exceeds this value so that internally, the BMS can recalibrate when all balancing has been completed.
Warnings from Victron might be triggered when these parameters are turned on:
| Battery High Voltage Warning | If you enable critical > Cell Volt High |
| Battery Low Voltage Warning | If you enable critical > Cell Volt Low |
| Battery High Temperature Warning | If you enable critical > Cell Temperature High |
| Battery Low Temperature Warning | If you enable critical > Cell Temperature Low |
| Battery High Temperature Charge Warning | If you enable charge > Cell Temperature High |
| Battery Low Temperature Charge Warning | If you enable charge > Cell Temperature Low |
| Battery High Current Warning | If you enable critical > Shunt Charge Amp High |
| Battery High Charge Current Warning | If you enable critical > Shunt Charge Amp High (same rule) |
| BMS Internal Warning | No communication was established with the BMS |
| System Status (Online/Offline) | Is Critical Batt Ok status |
.png)